You have to be careful putting a UPS into a rack enclosure/data hall (ie not do it). UPS rooms are separate to data halls for a reason. Tier IV recommends at least two hours fire rating between power infrastructure and data halls. USP systems and batteries should be checked at least twice yearly and terminal torques at least every few years.
Batteries are a self contained ignition source. This means that you can put a fire out and it will come back. Data halls tend to be protected by an inert gas which once discharged has to then be refilled. This means if you had a battery fire in a data hall the gas would discharge and then if the a battery reignited there would be nothing to stop it and you could lose all your data. This is also why gas suppression in a battery room has limited benefit without automatic link breakers (ie reduce the voltage in the string).