It's an interesting fact that many aircon systems can't cope with air that's too dry - such as in server rooms. This is is issue when people just buy an off the shelf system designed for comfort cooling in occupied spaces and use them for the server room, or re-purpose a small office as a server room.
The reason is down to the energy that needs to be extracted to condense water vapour. If the air is wet, much of the cooling energy goes into condensing water and the evaporator coil stays relatively warm. With dry air, there's a similar level of cooling ability, but now it's just cooling the air - so both the air coming off the coil, and the coil itself, are much colder. The result is often that the water that does condense will freeze on the coil before it can run off - with the result that the coil blocks up.
And worse, as the ice interrupts the airflow, that bit of the coil will get colder still and the ice will spread to adjacent fins. Eventually, all airflow stops, and the coil is encased in a block of very cold ice. It takes a lot fo energy to unfreeze it - just getting it up to freezing temp takes a lot of heat (which is hard to get into the ice), but then you need to supply the latent heat of fusion to melt the ice.
A decent control system will detect this problem and switch off the compressor while leaving the fans running - or even reverse the cycle to heat the coil that would normally be cooling. In smaller systems (like a freezer), there may be an electrical heater. I recall Land Rover Defenders of 80s/90s vintage with the option air con would freeze up in hot desert conditions - the fix being to turn them off for a few minutes every so often and let the airflow melt the ice out, but you have to do that before the ice completely blocks the airflow.
All this should be a "past problem" - these days all systems should have sensible control systems that will detect and fix any icing without the user noticing.